I'm designing a grocery store.  I have reviewed chapter 5 of the 50% AEDG for grocery stores and found that I can use the SZVAV DX with DOAS (HV6). The guide states that I should meet or exceed the efficiency levels in table 5-16. I have a 26 ton RTU (312 Mbh) which is large than the highest listed with an efficiency 240 Mbh. The table just says "not recommended" if >240 Mbh. In the Climate zone 4 recommendation for my SZVAV DX Package RTU with DOAS there is also a maximum external static pressure listed a 0.7 in w.g.

Will this large (312 Mbh) system be acceptable for the prerequisite? Will I be able to get any additional points in Eac2 if I don't reduce the size and provide two separate systems under the 20 ton (240 Mbh) size limit? With the larger RTU I also have designed 1.0 in w.g., is this and issue? The not recommended is ambiguous