Forum discussion

NC-2009 IEQc5:Indoor chemical and pollutant source control

Advice on acceptable approach to credit achievement for IEQc5

Is a covered exterior grate system (e.g, outside a vestibule) at all high volume entryways an acceptable approach to credit achievement for IEQc5? Any advice or guidance would be most appreciated. Note that our project is pursuing LEED v1.0 NC certification through the CaGBC.

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 11/25/2011 - 08:18

Hi Shelley, In my opinion unfortunately not. User guide has on page 513 description of entryway systems says that: "entryway system must extend 10 feet from the building entrance into the building interior..." Of course you can go threw special circumstances path bacuse it might depend i.e. on project location or design of entrance overhang.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.