How can we separate metering for cooling an ventilation if they are both within the same unit ?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $15.95 »Forum discussion
NC-v4 EAc3: Advanced energy metering
How can we separate metering for cooling an ventilation if they are both within the same unit ?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $15.95 »To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5927 thumbs up
September 6, 2023 - 8:53 am
You can often separate cooling energy use and fan energy use through the BAS. If you set up the BAS to monitor the fan operation you can calculate energy use from that data. That said I think that if they are both in the same unit LEED would allow you to meter the whole piece of equipment and not require that you separate them.
Dave Hubka
Practice Leader - SustainabilityEUA
LEEDuser Expert
542 thumbs up
September 6, 2023 - 9:17 am
The numerous editions of the v4.1 reference guides over the years all seem to state "there is not substantive changes to the credit requirements, refer to the LEED v4 reference guide."
The v4 reference guide allows metering of one unit (e.g. Rooftop unit, heat pump, furnace, etc..) as an acceptable way to achieve the credit. Read through the FURTHER EXPLANATIONS - Determining Major Energy End Uses section, it gives pretty detailed guidance in this situation.
This is not one of my typical credits, but I have had success with GBCI reviews when project teams submeter each energy source (e.g. gas & electricity) to each single packaged equipment such as a rooftop unit.