Healthcare-v4 EAc3:Advanced energy metering

Advanced energy metering required for LEED when exempted by energy code?

Our building is following ASHRAE 90.1-2016 for code compliance purposes.  Under section 8.4.3 Electrical Energy Monitoring, there is an exception for "Critical and Equipment branches or NEC Article 517."  NEC Article 517 is a section of the electrical code is for Healthcare facilities.  The Critical branch typically includes hospital "red plug" receptacles, any equipment directly related to patient care, nurse stations, lab equipment, medicacl storage, etc.  The Equipment branch typically icludes HVAC equipment, med gas pumps, kitchen equipment, etc.

Because the energy code exempts these electrical loads from having to be metered, recorded, and reported, does a similar exception apply to this LEED credit?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sat, 03/11/2023 - 00:37

For LEED you have to model all energy use. Typically this stuff would get lumped in with the regular plug load which will be more than 10%. You could model these loads separately and if they don't add up to 10% you don't have to sub meter them.