I'm working on a LEED-CI offices project. I'd like to apply additonnal interior lighting power as specified in ASHRAE 90.1-2004 section 9.6.2b: Lighting to be installed to meet the requirements of visual display terminals. So I assumed that a computer is a visual display and the user needs more lighting for his work. So we are using a T8 luminaires under desk shelf. To have additional power accepted, the luminaire must meet specific requierements. ASHRAE specify a maximum luminance of 80cd/ft² at 65 degrees. What the ft² refer to? Area of the desk, the floor, the luminaire? It is unclear...
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Is your project under LEED ID+C 2009? If so the 2004 version of 90.1 does not apply. The additional lighting you mentioned is not available in the 2007 version of the standard.
My project is in Canada. LEED Canada is a little behind and still refer to ASHRAE 2004, so additional lighting may apply. Do you know this version and what they mean about this luminance?
This requirement is related to glare in the vertical plane. So the square footage is in the vertical plane below the fixture.