Do we need to know and submit the actual VOC content of adhesives and sealants? A manufacturer does not indicate the actual VOC content on its MSDS and certification, only the statement that the products do not exceed the maximum VOC limits set by SCAQMD Rule 1168. Do we still need a laboratory certification indicating the actual results of the VOC analysis to comply with this requirement?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Tristan Roberts
RepresentativeVermont House of Representatives
LEEDuser Expert
11478 thumbs up
July 27, 2010 - 11:06 pm
An MSDS, cut sheet, or letter from the manufacturer is sufficient to verify the VOC content—a lab certificate is also sufficient but not needed.The documentation requirements are discussed above under the Checklists tab, under Construction Documents. If you don't have an actual VOC number, but the manufacturer says the product is compliant, that's okay, but you have to assume that the VOC number is at the threshold, e.g. if the limit is 150 g/L, assume that the product is 150 g/L.