Our project features a building that has an open concept with glazing all along the exterior. The interior offices are typically encased in glazing to further allow access to natural light. When calculating the Daylight Factor for these interior offices I am considering using the following method I have seen described else where:

Use the visible light transmittance of the exterior glass and multiply it times the visible light transmittance of the interior glass of the interior room.

Then use the area of glass of the room with the borrow light glass in it just as if it was on an outside wall. This should reduce the amount of useful light in the internal room receives due to the day light's passage through exterior glass and then interior glass.

A sample of the calculation would be as assuming fairly high visible light transmittance
glazing:

• Visible light transmittance, exterior double glass (possibly low-e, untinted) = 0.69
• Visible light transmittance, interior single glass, clear = 0.81
• Useful visible light transmittance (of internal room) = 0.69 x 0.81 = 0.56.

can anyone advise if this is an acceptable approach?