CS-2009 IEQc8.1:Daylight and views - daylight

about the draws in 8.1 and 8.2

Hello i am working on IEQ 8.1 and 8.2, I use simulation methods in 8.1. my question is that can i use diffrient draws in two credit? in 8.2 i used draws include finish and patitions, but in 8.1 i used the draws do not have these, just floor plan.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 08/13/2013 - 12:52

Any un-moveable partitions must be consistently included in all LEED credits. If these are moveable partitions, then they do not need to be included in the calculations. If you are using the actual tenant fit out plans, then they should be used consistently. If they are the proposed tenant fit out plans, you can use different plans, but ensure that the tenant lease agreement and/or guidelines indicate the methods by which the tenant must use to maintain the daylight levels and views.