FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

90.1 Mandatory Provisions

Does Appendix G or LEED modeling protocol require the baseline building be modeled with all of the mandatory provisions of Section 6.4? And if so where is this stated? Appendix G implies it, but it is never specifically stated. Other mandatory provisions are specifically identified in appendix G (specifically envelopes, DCV, etc). Even the DCV reference only states that you ventilation rates must match in each model except in areas with DCV not required by 6.4.3.9. Meaning that the model doesn't necessarily have to comply with the mandatory provision, but it can't show savings against this requirement. Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 10/20/2015 - 17:38

Appendix G does not necessarily require compliance with all the mandatory provisions. It defines the Baseline. LEED projects (Proposed design) are required to meet all the mandatory provisions and this is stated in the credit language.

Tue, 10/20/2015 - 18:29

I understand the proposed design has to meet all of the mandatory provisions, but does the modeled baseline? In particular, I am performing a App G analysis for 90.1-2010 for a government project and in accordance with LEED Interpretation 10421. For 90.1-2010 6.4.3.10 requires single zone units that are large enough be VAV. Does this requirement apply App G baseline systems 3&4 of large enough size?

Tue, 10/20/2015 - 18:40

As I indicated no it does not. System 3 and 4 remain constant volume in the Baseline model.

Wed, 10/21/2015 - 20:45

Thank you.

Wed, 02/05/2020 - 17:14

Hello, I have almost the same question but this time concerns the building envelope. Could you tell us if it is mandatory that the thermal coefficients of my building comply with table 5 - 5.3 of ASHRAE 90.1 which governs the performance of each type of envelope? I'm lost...We are working for a project outside the United States.

Wed, 02/19/2020 - 20:41

Hi Sara, As Marcus already noted, that table is not mandatory if you are following Appendix G. ASHRAE 90.1 is very tricky, you need to follow the diagram at the beginning of each section. In page 17 of the Standard 90.1-2007, after Section 5.4 you can choose between Sections 5.5, 5.6 or 11. Since you are using energy modelling, you jump to Section 11 and then to 5.7 (you skip sections 5.5 and 5.6).