FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

90.1 - Air-side Economizer & Humidity Requirements

I have a 90.1 App G. interpretation question. G3.1.2.6 requires economizers in certain climates. The only exceptions are for gas-phase air cleaning and supermarket open refrigerated cases. I have a project in climate zone 5A (Boulder) with a server room. The server room has a 50% +/- 10% relative humidity requirement. I have not designed an economizer in the space because of this humidity requirement. 90.1 is requiring an economizer in this space. I have four options: A. Put economizer with the humidity requirement into the baseline. This causes the energy use to go way up due to the humidifier. I feel like I am unfairly manufacturing savings in this scenario. B. Remove the humidity requirement from the space in both the proposed and the baseline, and only economize in the baseline. I feel like I'm being unfairly punished in the proposed model in this scenario. C. Remove the humidity requirement from the space in both models, and economize in both models. This is modeling economizing in the proposed that doesn't exist, but I feel like this is just removing any savings or punishments from the model. D. Keep the humidity requirements in both models, and have no economizer in both models. This seems the most practical. Once again it removes any unfair savings or punishment from the analysis. However, this goes directly against what 90.1 App G says in G3.1.2.6. Any ideas? Thanks.

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 04/03/2012 - 14:17

The Proposed model is as designed and constructed, so B & C are out. A - technically follows Appendix G. However this gets tricky since the humidification is related to a process load and not for comfort. If you look at Section 6.5.1 there is an exception related to humidification above a certain level. D - agree that this is the right approach. If questioned in the review process you can justify it based on the fact that it is process load related and is also a conservative (limits the savings) approach.