FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

90.1-2007 Addendum dn

Does anyone have experience modeling this for LEED EAp2/c1? We have a warehouse project with gas-fired heat only MAUs (about 35,000 cfm total) and 100,000 cfm of what I'd define as non-mechanical cooling exhaust fans (per the addendum) which draw OA in through louvers for 'cooling' in the summer. Unfortuantely our proposed building combined fan power is about 3x higher than the calculated baseline fan power as required for Systems 10 and 11 per appendix G. What am I missing here...

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 10/10/2011 - 16:11

Sounds like a modeling issue maybe more appropriate for the forums at onebuilding.org.

Tue, 11/11/2014 - 16:23

Hi, That issue occurs now in our project too. We have a heated-only production hall and warehouse with the supply air flow 150,000 cfm and 14,000 cfm. The System 11 per 90.1-2007 Addendum dn has a very low SFP (0.3W/cfm). If we simulate the baseline system with system 11, the proposed building fan power is about 2x higher than the calculated baseline fan power. I tried to find some information or suggestion at onebuilding.org, but unfortunately I don’t have found anything about this problem. Is that allowed to use another system type per 90.1-2007 (e.g.System7) and set the cooling coil ‘no duty’ or a higher upper limit of the room temperature that will never reached. Many thanks in advance!

Tue, 11/11/2014 - 17:46

You are not required to use the heating only systems. You can get around the requirement for installing a cooling system by citing the fact that you can simply set the temperatures so that the cooling system would never operate. So you can actually model it that way with a cooling system but this is really a waste of time. We have had success simply explaining that we have not modeled a cooling system because we could set the temperatures high enough that it would not operate and achieve the same effect without modeling the cooling system at all.