Appurtenances such as HVAC equipment, etc., can be excluded from the calculations. Good news for your project.
Does this mean if the building 100' x 100' for example = 10,000 sq/ft total roof surface, you will use 10,000 sq/ft as your total roof sq/ft. even though your roof may only be really covered by 50% SRI membrane and the other 50% HVAC appurtenances, etc...??
When you're documenting this credit in LEED Online, the form asks you to provide total roof area "excluding mechanical equipment, photovoltaic panels, and skylights)." So, you're not entering total roof area, you're entering total roof area that is eligible for consideration under the credit. You're also uploading a roof plan and other documentation. Make sense?
That makes perfect sense Tristan. What doesn't make sense is that when LEED asks for the SF (from LEED;Note that in the table below, 'Square footage' refers to the actual area of roof covered by the SRI surface) and then asks for "Total roof area (excluding mechanical equipment, photovoltaic panels, and skylights) (sf):"
and then I calculate I get a number of 243.55%. Because my the overall SF is 5932 sf and the number excluding the appurtenances is
2591.75 I come out with that strange number.
LEED's response was this;
Response: The information provided above indicates that the area of White EPDM (5932 sf) exceeds the total roof area (2591 sf). This information would indicate that the reported square footages may be incorrect and would indeed result in > 100%. Perhaps the numbers are switched? Also, please note that the calculation for the SRI compliant area is weighted based on the SRI value. Therefore, when using high SRI materials, it is possible that this calculation will demonstrate > 100% compliant roof area.
I guess what they are saying is that it is okay to have a 200+% number. Does that make any sense to you? If it does I have completed this credit.
You didn't mention your SRI values, but if they're higher than the minimum requirements, it's not surprising that the weighted value would generate a weird-looking percentage number.
Just to be sure....table SSc7.2-1 asks for the total square footage of the reflective material. And THEN it asks for the total square footage of the roof MINUS the solar panels, skylights and mechanical equipment. I have entered in the relective material square footage which is a larger number than the square footage minus the appurtenances. And this will be okay? Shall I upload a spreadsheet with all the square footage numbers in it (total roof, roof minus LEED-allowed appurtenances, roof minus terrace and other "non-roof" surfaces, etc)?
Andrea, I don't see how the SF of your reflective material could be larger than the SF of the applicable roof area. It implies that some of the area you are counting as appurtenances actually has relfective roofing on it. Or am I misunderstanding something?
Exactly, Tristan. Our RTU-1 rooftop unit (5794 square feet) actually has the reflective roofing on it. I should be okay, right? I uploaded a very clearly labeled Google Earth map.
Yes, that sounds okay. Hopefully everything is clear to the reviewer and you don't have any difficulties.