FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

6.4.3.4 Ventilation System Controls

To comply with the mandatory sections 6.4.3.4 “Stair and Shaft Vents” and 6.4.3.4.2 “Gravity Hoods, Vents and Ventilators”, according to the climate zone 2, the standard requires that gravity dampers are installed in every outdoor air intake, exhaust hoods, stair and elevator shafts vents. I’m working in a project that operates 24 hours. The HVAC system designed treats the air before supplied to every floor AHU. Every duct that supplies the air to the AHU has a constant air volume damper. The stairs were designed with pressure sensors and a VFD fan that regulates the volume of air supplied in the stairs according to the outdoor air demand. I would like to know if the system designed, as described above, complies with the mandatory sections 6.4.3.4 and 6.4.3.4.2, i.e., without gravity dampers. If not, what should we do to comply with these sections?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 12/03/2012 - 19:39

Sounds like motorized, not gravity, dampers are required under 6.4.3.4.1. 6.4.3.4.2 requires that all outside air intakes and exhaust have motorized dampers (unless exception a applies then gravity dampers are OK). Sounds like you need to install dampers if they are not included. The reason they are required is that just because it is a 24 hour operation now does not mean that could not easily change.

Tue, 12/04/2012 - 12:39

Hi Marcus, The project is a hospital where it will always operates 24 hours and the exception A is applied (the project is on the zone climate 2). Does that mean the project doesn’t need to have any kind of damper or gravity damper still needs to be installed? Thanks for your help!

Tue, 12/04/2012 - 14:40

The way I read it you are required to have dampers. Either motorized or gravity would comply. I do not see any exceptions that apply.