FAQs about EQp1 :

We have a VAV system where single AHUs serve multiple zones. Do we need to take outside air measurements at each VAV box?

Our building has a single fan that supplies outside air to multiple AHUs. Do we need to perform outside air testing at the supply fan or at all AHUs?

What if our systems do not meet the required outside air when systems are tested at worst-case conditions?

What if after our Preliminary Review we have to revise the ventilation rate procedure calculations and find that we need to make corrections to the system in order to meet the prerequisite? Can we redo the outside air testing after making corrections? Wou

My building has 80 AHUs providing ventilation to building spaces. Do I have to do the ventilation calculations and conduct outdoor air measurements for each one?

Our system cannot provide enough outdoor air to meet ASHRAE 62.1-2010 due to design limitations. How much outdoor air must we provide to meet Case 2 instead?

The outdoor air intake for our ventilation system is not accessible, and it’s not possible to measure the outdoor airflow directly. How can we determine the outdoor airflow for this system?

How do I find whether my project is located in a non-attainment area for particulate matter or exceeds the prerequisite ozone requirements?

What happened to the IEQ Space Matrix that was available to version 2009 projects? What should I reference to determine how spaces in my building should be categorized for this prerequisite?

View answers »

Forum discussion

EBOM-v4 EQp1:Minimum indoor air quality performance

62MZ Calculator for v4

The prerequisite form states that 62MZ Calculator can be used as an alternative to Minimum Air Quality Performance Calculator and it can found under the prerequisite's Resources tab in the Credit Library. However when you visit LEED Credit Library there is no 62MZ Calculator available anymore. Does that mean that only Minimum Air Quality Performance Calculator is now used for VRP calculations and 62MZ Calculator is not accepted anymore?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 02/28/2017 - 17:11

From my experience, GBCI is not accepting ventilation calculations performed on the 62MZ calculator for v4 projects. I don't believe they are accepting the 62MZ calculator on v3 projects either but cannot confirm. After a discussion with GBCI, it was confirmed that there were some issues with the 62MZ calculator, hence they since have provided an updated ventilation calculator.

Add new comment