NC-2009 IEQc2:Increased ventilation

30% for all spaces individually or for the total ?

We have an overall 30% ventilation above ASHRAE, but it is different in each spaces. Some spaces have 10% more and other have over 40% more. For credit compliance do we need 30% on the total ventilation, or do we need to have 30% for each individual zone?

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 12/02/2011 - 18:33

Every space needs 30% over

Tue, 04/10/2012 - 20:43

FYI - This has been updated with the latest forms. Now you are able to enter just the total OSA for a system. This allows you to share OSA throughout the zones associated with each system. However, you still need to be aware of your zone Zp (ratio of OSA to Minimum Supply Air in a zone) as it can significantly raise your OSA requirements for a system.