CI-2009 IEQc3.1:Construction IAQ management plan - during construction

100% Outside Air systems

The base building HVAC system uses 100% outside air. Therefore there are no return grilles. I am assuming that the requirement for filtration then is not applicable?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 09/09/2015 - 15:07

If there is not a way for contaminants to get back into the ventilation system, you would meet the intent, and I would assume you are right. However, I'd prefer that mechanical engineer answer this question.

Thu, 09/10/2015 - 23:37

Thanks Michelle That's correct for this credit - but you'll also need to meet the ASHRAE standard minimum of MERV 6 before a cooling coil (if applicable). IEQp1 requires that you meet ASHRAE standards. I'd recommend MERV 8 anyway - they are practically as cheap and similar pressure drop.