Forum quick links
Redoing MRT measurements after preliminary review
EBOM-2009 IEQc2.3:Occupant Comfort—Thermal Comfort Monitoringposted by American University on
GBCI pointed out to us during their preliminary review that one of our past engineers did an air temp reading in sample spaces rather than a mean radiant temp reading.
Sample size for air speed measurements
EBOM-2009 IEQc2.3:Occupant Comfort—Thermal Comfort Monitoringposted by Peter Locke on
Does anyone have a comment on the number of spaces (% of spaces?) that an air speed sample would need to include?
Tenants
EBOM-2009 IEQc2.3:Occupant Comfort—Thermal Comfort Monitoringposted by Gustavo De las Heras Izquierdo on
Does anyone know if all the tenants need to be included in this credit?
HVAC zone
EBOM-2009 IEQc2.3:Occupant Comfort—Thermal Comfort Monitoringposted by Gabriel Frasson on
I have a project that has fancoils separated by floor.
No BAS.
EBOM-2009 IEQc2.3:Occupant Comfort—Thermal Comfort Monitoringposted by Melissa Young on
As it says above, achieving this credit without a BAS is difficult. What exactly needs to be done if we don't have a BAS?
skipping RH sensors and getting IEQ 2.3?
EBOM-2009 IEQc2.3:Occupant Comfort—Thermal Comfort Monitoringposted by Allen Doyle on
Is it possible that a climate could be benign enough that RH sensors would be redundant or unnecessary, and a project would still gain IEQ 2.3 compliance with temperature monitoring alone? In our s
humidity sensors "for" occupied spaces or "in" occupied spaces
EBOM-2009 IEQc2.3:Occupant Comfort—Thermal Comfort Monitoringposted by Jean Marais on
The credit language says "in", but could it mean "for".
Radiant Temperature Measurement
EBOM-2009 IEQc2.3:Occupant Comfort—Thermal Comfort Monitoringposted by Sonrisa Lucero on
In the picture on the "Bird's Eye View" page, there is a picture of an infrared thermometer. This would take the temperature of an object.