I would like to know if there is a maximum obstruction height of views for option 1. In the case in my project, if it is an office building, with a central atrium and in that atrium, we would have a window-sill of masonry and just above a frame of transparent glass. I would like to know if there is a height limit for this window-silll which is not considered obstruction.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
TODD REED
Energy Program SpecialistPA DMVA
LEEDuser Expert
891 thumbs up
August 28, 2017 - 7:30 am
There is no set height limit for sills. If a sill is somewhere in the 6' range, then you could not use the area within 10' of the window as having views. A person's cone of vision spreads out, so higher heights still provide views to those at a distance. If you have people working close to the window wall, then you should have a sill height around 42"