Forum discussion

NC-2009 WEp1:Water use reduction

Water Use Reduction Baseline for Renovation

My office is working on a school renovation registered under LEED v2009 NC. I am wondering what the baseline water usage is for new plumbing fixtures replacing fixtures that were installed in the 1980s. Example, is 1.6 GPF for water closets still the baseline or would the baseline be what the original fixtures being replaced is? Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 12/08/2016 - 15:22

Hello John, Yes, the baseline flow rate for water closets is 1.6 GPF. Projects must utilize the baseline flow rates outlined in the LEED 2009 BD+C Reference Guide (and not the flow rates for the current fixtures installed).

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.