Forum discussion

NC-2009 EAc1:Optimize energy performance

VRV and ASHRAE 90.1-2007 and 189.1 Standards

Hi all. I´m working in a project with VRV and want to specify a system with high COP values, and three issues surfaced.... 1- Since there is no exact system specified in the ASHRAE 90.1 that matches the VRV system, I have been told to model the VRV system using the efficiencies in Table 6.8.1B. However these efficiencies are typically for full load operations, so it will not capture the advantage of the part load capability of the VRV systems. Therefore, the savings calculated will be typically conservative. 2- Can I compare a VRV with the effciency of a chilled water system? 3- Or do you think it is a good idea to at least use Table C-2 values from ASHRAE 189.1-2009, with higher COP values? I want to include minimum COP values within the technical specifications. We are just indicating system size, capacity, etc, and no brands / models. Therefore, we want to make sure we get a system with high energy efficiency values. Any thoughts?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 03/22/2013 - 15:05

Sonia the following answers apply to your questions as follows: 1.Depending on the software you are utilizing you can model (for your DESIGN CASE) a VRV system adequately with or without "fixes". The followinng links may help you with eQUEST and/or energy plus. Energy Pro, which is used in California has VRV libraries included. http://www.google.com.mx/#hl=es-419&sclient=psy-ab&q=energy+plus+vrv+system&oq=energy+plus+vrv&gs_l=hp.1.0.0i30j0i8i10i30.4309.19737.0.23369.15.14.0.1.1.1.1045.4099.2-2j4j1j0j1j1.9.0...0.0...1c.1.7.psy-ab.v8XiNmBdIHs&pbx=1&bav=on.2,or.r_qf.&bvm=bv.44158598,d.b2I&fp=f06a09c846aeaaee&biw=1366&bih=622 http://www.google.com.mx/webhp?hl=es-419&tab=ww#hl=es-419&sclient=psy-ab&q=equest+vrv&oq=equest+vrv&gs_l=hp.3..0i30l2j0i8i30.2537.5526.0.7138.10.9.0.0.0.1.2329.5962.2-1j1j3j8-1j1.7.0...0.0...1c.1.7.psy-ab.l3pzbpq9AQE&pbx=1&bav=on.2,or.r_qf.&bvm=bv.44158598,d.b2I&fp=f06a09c846aeaaee&biw=1366&bih=622 In short you end up modeling a Heat Pump system with a custom performance curve, sounds simple but does equate into some effort. 2.When you are referring to comparing I am assuming you are performing LEED calculations, if so you have to compare to the BASELINE definition in ASHRAE 90.1 Appendix G table G3.1 3.

Fri, 03/22/2013 - 15:11

I am told Trace 700 runs VRV/VRF systems and two manufacturers have data to assist with setting it up in Trace and another in EPro Plus.

Fri, 03/22/2013 - 16:01

Guidance on the minimum efficiencies for VRV systems can be found in ASHRAE 90.1-2010.

Mon, 03/25/2013 - 18:20

Thanks Guys!. Jorge and Robert, we are definitely doing a energy simulation using Trace and Energy Pro (who does VRV modeling). We want to see how the same building compares...For know I just wanted to have an idea on COP values, botn minimum and "more efficient". I also checked the ASHRAE 189.1 standard and Marcus, thanks for the info regarding ASHRAE 90.1 2010.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.