Forum discussion

EBOM-2009 IEQp1:Minimum indoor air quality performance

VRP Compliance Calculator

Hi together, I have a question about using the VRP Compliance calculator. Have I only to consider occupied spaces respectively spaces which are intend to be occupied. Or have I to consider all areas which are mechanically ventilated (corridors, sanitary rooms, storage rooms, lift lobby, etc.? And where I have to measure the outdoor air intake flow? On the main inlet on the roof or on other positions like distribution? Thanks in advance for any help.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 05/31/2013 - 21:58

Tajo, Occupied spaces only. So no storage rooms, mechanical rooms, electrical rooms, etc. But you should include lobbies, corridors, etc. You need to measure the outdoor air intake flow at the unit (the main inlet on the roof in you situation). This will give you a % of OA to use for your calculations. You need to know the distribution air flows as well, but if you have old design documents or read the values off the terminal unit that can suffice.

Wed, 07/17/2013 - 18:24

Table 6.1 ASHRAE 62.1 does include outdoor air rate for the area component for storage areas, electrical rooms, and elevator rooms. However further clarification is provided here. http://ashrae.org/File%20Library/docLib/Public/20100203_ic_621200717.pdf

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.