Views for an Apartment Building

I'm working on documenting this credit for an apartment building but have a question about documenting it. Most of the floors are identical in terms of rooms square footage and layout. Do I have to document each room separately, or is it possible to combine similar rooms into one entry if they are identical on multiple floors? Thanks!

6

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 04/25/2011 - 12:25

Hi Lauren, It will be easier for the review team if you list each floor, but understandably if you have a lot of the same/typical floor plans then it is acceptable to combine, or rather list "Floors 1 - x (typical)" as a line item in your views calculations with the results. Just make sure your regularly occupied total square footage for IEQc8.2 matches the square footage listed throughout your project documentation and I would simply include a brief narrative for the reviewer confirming which floors have the exact same layout and square footage just to be clear. Hope helpful!