Forum discussion

CS-2009 IEQp1:Minimum indoor air quality performance

Ventilation Openings

Hello. We are working on a Core & Shell project, it has retail spaces that consists of two levels each one. On the second level, openings will be included in order to ensure the needed ventilation air rates but on the first level nor openings exist or will be included. Can we consider the entrance door (due to it is always open during occupied hours) as the opening area required for ventilation? or, Do we have to make architectural changes in the retail spaces facade in order to fulfill the ventilation air rates? Thanks in advance.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 09/12/2012 - 01:23

Yes the first floor would need to meet the LEED ventilation requirements. It sounds like you are attempting achieve the requirements by Natural Ventilation. In this case you need to meet the requirements of ASHRAE Standard 62.1-2007, Paragraph 5.1. (Naturally ventilation spaces shall be within 25 ft of operable wall, the openable area shall be 4% of the net occupiable floor area...). Depending on the size of the space the entrance door may not be enough.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.