Hello all,
I am completing the 62mzcalc spreadsheet during heating mode. VAV box minimums are typically 30% for systems with reheat. My system is cooling only, so i define my VAV minimums to a value higher than 30% with the largest being 55% to be able to reduce the system ventilation air. Is this an acceptable approach?
Also, if a VAV serves 3 rooms and only one of these rooms is my critical zone, and i raise the VAV minimum for example to 40% for this room only to satisfy its ventilation, I will have to input the same VAV minimum (40%) for the other two rooms, even if they do not appear as critical, correct?

Appreciate all opinions and advise on this.