NC-2009 EAc1:Optimize energy performance

Variable Speed Fan Coil Unit

There are more and more companies making fan coil units with VFD motors, automatic variable supply air control rather than traditional 3-speed control, which gives them variable air volume capability similar to the typical VAV system (VAV box/terminal unit). So can variable speed FCUs be treated as VAV systems in the energy model? Under 90.1, our system should be compared with System 8 VAV with PFP box, but I think it would be unfair to us if we just model it as a constant volume system.

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 11/15/2011 - 14:58

Not sure I understand the question. Model the Proposed as designed and the Baseline according to Appendix G. The Appendix G Baseline system does not change based on the details of the Proposed system.

Wed, 11/16/2011 - 02:58

Well, What I meant is can we call these "variable speed FCUs" a VAV system then? Because normally when you say VAV it means constant SA air temp fitted with "VAV box", not a hydronic system such as FCUs.........

Wed, 11/16/2011 - 03:19

Normally you would treat FCU as a constant speed CAV system, and it would be disadvantageous to us if this is compared to, in the case of our baseline, a VAV system in the energy model. So I need to know if we can call our proposed system as a VAV system.

Wed, 11/16/2011 - 13:59

You should model what you have designed in the proposed. How you model it depends on the simulation program. They are all different. In general you cannot model a FCU as a VAV as there tend to be significant differences between the two. Sounds like you are asking if modeling the variable FCU as a VAV would be an acceptable workaround in the software you are using. If that is correct I would suggest you post your question on one of the simulation software discussion groups at onebuilding.org.