In this pre-requisite we are following 'Option A' and filling in details in the 2007UM_62MZ Calculator.
Further,filling in the online template column 3 in Table 1.1 requires "Minimum required outside air flow,CFM".I am not able to identify which value has to be input for this column.Is it derived from 2007UM_62MZ Calculator?
Please Advise.Thank You.
Jenny Carney
Vice PresidentWSP
LEEDuser Expert
657 thumbs up
July 30, 2010 - 12:59 pm
Is this a v2008 or v2009 project? I ask, because the v2009 forms have been undergoing some changes in terms of what inputs you need to provide.
But, to answer your question, you can find the required OA in the 2007UM-62MZ calculator in cell I 35 ("Outdoor air intake required for the system")
Yong Lee Low
ESD ConsultancyZEB-Technology Pte Ltd
179 thumbs up
August 24, 2010 - 6:09 am
Thank You.Mine is a 2008 version.There are only limited categories under which we can input space usage.For. eg. in a hotel if we have changing rooms,toilets etc.,what space use to allocate to such spaces?
Jenny Carney
Vice PresidentWSP
LEEDuser Expert
657 thumbs up
September 28, 2010 - 10:12 pm
Restrooms are subject to exhaust rate requirements, not OA rates. You can find the criteria in Table 6-4 of the standard.