Is this a v2008 or v2009 project? I ask, because the v2009 forms have been undergoing some changes in terms of what inputs you need to provide.
But, to answer your question, you can find the required OA in the 2007UM-62MZ calculator in cell I 35 ("Outdoor air intake required for the system")
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Thank You.Mine is a 2008 version.There are only limited categories under which we can input space usage.For. eg. in a hotel if we have changing rooms,toilets etc.,what space use to allocate to such spaces?
Restrooms are subject to exhaust rate requirements, not OA rates. You can find the criteria in Table 6-4 of the standard.