Hello;
Out BAS does not measure air flow (CFM), but, it does measure Return Air and OA C02 values.
Can this PreReq be met using CO2 measurement (demand ventilation) rather than CFM? If so, how can it be done?
thanks
Forum discussion
EBOM-2009 IEQp1: Minimum IAQ Performance
Hello;
Out BAS does not measure air flow (CFM), but, it does measure Return Air and OA C02 values.
Can this PreReq be met using CO2 measurement (demand ventilation) rather than CFM? If so, how can it be done?
thanks
LEEDuser is supported by our premium members, not by advertisers.
Go premium forTo post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
David Hubka
Director of OperationsTranswestern Sustainability Services
527 thumbs up
March 30, 2011 - 1:51 pm
The prereq requires an airflow measurement.
CO2 sensing of RA and OA will not suffice.
sorry :(