Upload IEQc3.2-1. Provide the IAQ Management Plan...

Hello, I have been successfully completing IAQ Testing under Option 2 for a few years now and always wondered about this section of the credit template. It states to "Provide the IAQ Management Plan for the project building with IAQ management practices implemented during construction highlighted." I always over looked this section and assumed it applied to IEQc3.1 and was administered by the general contractor. I have since taken the time, while uploading a project I am currently working on, to re-read this section at the beginning of the credit template and noticed it mentions this in the LEED guide as well under IEQc3.2. I guess the question I am posing is whether anyone has an example of this documentation? As the testing PM/technician, it seems this would be more appropriate for the construction team to document; which is the approach I have taken on all projects in the past. Thanks! Zach

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 05/13/2015 - 18:40

the IAQ management plan during construction is most applicable to be the responsibility of the construction manager/general contractor. the documentation toolkit within this credit has a good example.