I have a building with two conditioned zones. One is dining and another is kitchen. Both zones has no wall and air can flow through each zone freely. Can I model both zones as one zone in the energy model, since the exhuast system of the kitchen will induce the air from dining zone? Thanks
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Maybe but I would guess not. Are they served by only one system? See also Table G3.1-7 and G3.1-8. A kitchen and dining area have very different thermal loads.
Dining area was served by 3 AHUs and Kitchen was served by 2 AHUs. One make up air unit serve both zone and the exhuast is located in the Kitchen. So, all the OA will pass from dining to kitchen through the counter area (large free area opening without door or window).
With this setting, it is hard to model them as separated zobes.
Can anyone help me on this?
Sounds like the remaining issue is how to model it. That tends to be very software specific. What software are you using?
eQUEST.
Yep eQUEST will not allow you do this air exchange between zones. So our thought would be to locate the OA and exhaust in the dining zone with the exhaust on the kitchen schedule. The kitchen would have no OA or exhaust.