I've looked deeply into all the comments here, but I can't seem to find an answer - I apologize if this is a repeat, or too simple of a question: My project has many AHUs, in some cases two different AHUs serve on space - some spaces are less than 5,000 square feet. Since all AHUs have a separate OA intake, am I required to do two tests in this one space since there are multiple AHUs?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 10/08/2015 - 20:40

Good question. Just one test for the room. It's the contaminants in the room from off gassing not the supply air quality.