NC-2009 IEQc3.2:Construction IAQ management plan - before occupancy

# Of Testing Locations

Our project single floor mixed use space, with a large single heat recovery unit providing outside air to all of the spaces. Additionally there are 17 plenum return heat pumps located throughout the spaces used to condition the air in the spaces. Since all of the spaces are normally occupied, would we be required to take a (1) IAQ sample or (18) samples (17 heat pumps & 1 HRU). Sampling method wont work for our type of building, but I'm curious if the OA serving the space is considered the ventilation system or if the heat recovery unit and heat pumps are all considered seperate ventilation systems.

4

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 08/22/2011 - 19:27

Daniel, Did you receive any comments in regards to this? This would answeer my question also. Thanks!

Mon, 08/22/2011 - 19:33

April, The general consensus I recieved was that this would require (2) seperate tests (one for the HRU OA zone and one for the Docking Bay served by Natural Ventilation), since the Heat Pumps are not Ventilation units based on ASHRAE mechanical design practices. Hope this helps.