FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

Schools-2009 EAp2:Minimum energy performance

Task Lighting

Dear all, I received the following review comment for my school project: "Tables EAp2.4 and EAp2.5 report consumptions for process lighting for both cases, but it is unclear what lighting has been included in this category and what exception(s) to Section 9.2.2.3 apply. Please provide descriptions of the lighting included in this category and which exception has been used, or revise the models as required. Keep in mind that Section 9.6.2 no longer includes an additional allowance for task lighting when using the Space by Space Method and that task lighting is not considered a process load." 1) Does anyone know of examples on what type of lighting may be included in process loads? 2) Does this mean that I need not worry about task lighting for all LEED projects? Many thanks,

4

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 11/21/2011 - 14:27

All of the Exceptions to 90.1 Section 9.2.2.3 are considered interior process lighting. No, task lighting must be modeled if it is in your project. It is not usually considered process lighting and should be included in the overall lighting for the Proposed model.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.