Forum discussion

NC-2009 IEQp1:Minimum IAQ Performance

System type

If a space is ventilated through an exhaust fan (rate according VRP) and a permanently open vent to the outdoors, can this space be considered mechanically ventilated, 100%OA and can use an Ez of 0,8 if exhaust fan is in the opposite side of the room of the vent?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/15/2015 - 15:24

According to Table 6-2, the above would be correct.

Tue, 09/15/2015 - 16:07

Thank you Andrew for the quick answer. I had this doubt because from some previous comments seemed that outdoor air should be provided by a supply system in order to consider the zone as mechanically ventilated.

Tue, 09/15/2015 - 21:12

Hi Andrew, 1.Is the project allowed to have operable windows instead of permanently opened vents? Air would infiltrate through cracks and doors. 2.The project will not be capable of providing MERV13 filters. Is the project still eligible to pursue credit IEQc5?

Tue, 09/15/2015 - 21:15

1. No, unless they are interlocked to automatically open when the fan is on. 2. No.

Wed, 09/16/2015 - 15:11

1.Is this requirement based in a LEED Interpretation or addenda? This would be very helpful in order to explain the client. 2.I agree.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.