FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

System Fan Power for System 8 VAV with PFP boxes

Hi everyone, I have to model system fan power in VAV with PFP boxes in accordance with Table G3.1.2.9 ASHRAE 90.1 2007. I calculate the system fan power with value of supply air (value calculated by software). Is this the sum of the supply fan, the return fan and the exaust fan powers? If I calculate the supply fan power in this manner, the return fan power as indicated in G3.1.2.8 (with 90% of the supply fan air quantity) and the exhaust fan power based on the exhaust air, when I fill these values in Table 1.4, the allowed fan power is just nearly half of the sum. I have also considered the Pressure Drop Adjustments. I have doubts about the fan calculations, because I use the same formula for three calculations. Could you help me? Thanks a lot.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 11/06/2015 - 14:49

The fan power calculation for the baseline includes the supply, return and exhaust fans. You can then divide this total among the various fans in the system. This is usually done in proportion to the proposed system if applicable. Only do the calculation once.

Fri, 11/06/2015 - 17:01

Thank you so much Marcus!