FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

System 5. Two boilers

In a review, the reviewer told me that as a system type 5, I should model 2 identical boilers. With that change (without defining capacity, I guess eQuest do it by demand) the baseline energy use decrease from 9 005 therms to 7 211 therms. As you can understand, this does not help in my purpose... and I cannot find a physical meaning. Anybody have a reasonable explanation? Thank you in advance

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/09/2014 - 14:58

It makes perfect sense. The single boiler would operate many hours at well under it rated capacity. It is even exaggerated by the required 25% over-sizing. Two boilers which are staged as required would more closely match the loads throughout the year. Since the boiler efficiency is lower when the loads are lower the energy use would be greater. This is why modular boilers often make sense from an energy perspective.

Tue, 09/09/2014 - 18:56

Thank you Marcus, I thought the boiler capacity was modulating under demand already with just one boiler. I have no defined any capacity for the baseline boiler, so I guess it was defined automatically by the eQUEST. Where can I find an explanation about how have to be defined this boiler? (more detailed than G3 reference to the two boilers). Thank you in advance.

Tue, 09/09/2014 - 19:05

The boiler must be auto-sized and a 1.25 multiplier applied to the capacity (see G3.1.2.2). The modeling of the boilers for the Baseline is described in several sections of Appendix G (see G3.1.3.2 to G3.1.3.6).