Schools-2009 IEQc7.2:Thermal Comfort—Verification

Survey for Sixth Graders

A comment that came back on our IEQc7.2 design review asked us to "Please provide confirmation that the survey will be administered to include all building occupants, including students of grades six and above". Our project is an elementery school (Grades pre-K through 6). The original submittal stated that the survey would be administered by the school districts superintendents office but we did not specifically state that it would be given to all adult staff and grade 6 students. Should we respond that the survey will be given to everyone listed or is it expected that we submit a separate survey directed specifically at the sixth graders.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 10/10/2014 - 15:30

Hi Matthew, Yes, confirm that the survey will be administered to those individuals. You also may need a different survey for the students, depending on how the questions are asked, so that it's not confusing for the students. For example, you may need to add a question that asks where in the classroom they sit most often (near window, back, front, etc...) and you may need to change some of the questions to refer to classrooms instead of offices.

Fri, 10/10/2014 - 15:45

Thanks, we'll add a survey to address a kids perspective on items like the one you mentioned.