You can claim a credit for diversity in two ways: one is short-term averaging (applicable to spaces like conference rooms or multi-purpose rooms that have intermittent occupancy); the other approach is the account for occupant diversity using the same factor used for sizing the block airflow for your VAV system (80% is typical). Plans and schedules are base submission requirements. You typically want to submit a spreadsheet showing ASHRAE 62 calculations in detail, especially if you don't have a decoupled ventilation system. Consider using the ASHRAE 62 calculation spreadsheet (available on LEED online).
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Thanks, Roger.
I couldn't find a way to show the short term averaging or the diversity factor on the Table at LEED online so I must submit my calculations in another form. We use HAP 4.5 from Carrier. Does it seem like they would accept that?
Bob, I would submit the HAP output, but also include a separate narrative clearly describing the calculation approach with references to relevant sections of ASHRAE 62. Did you have a look at the formal ASHRAE calculation spreadsheet? This is a separate thing from the LEED online letter template. The ASHRAE spreadsheet allows you to enter in factors for diversity.