In our project, a particular zone (Board Room) is being served by 2 systems: central chiller plant through an AHU & by Cassette Units. This additional system was introduced due to additional cfm requirement in that particular area. Please do let me know how do we need to zone this system in the VRP calculator and document.
Thanks
Nandana
Dylan Connelly
Mechanical EngineerIntegral Group
LEEDuser Expert
472 thumbs up
March 4, 2014 - 7:19 pm
Yes you need to zone the space in the VRP. Is the AHU's air ducted to the room directly or into the Cassette unit. If the former then just proceed as if the cassette is not there. It is just conditioning the air not changing the ventilation rates.