Forum discussion

CI-2009 IEQp1:Minimum indoor air quality performance

Single Zone served by 2 HVAC systems

Hi, In our project, a particular zone (Board Room) is being served by 2 systems: central chiller plant through an AHU & by Cassette Units. This additional system was introduced due to additional cfm requirement in that particular area. Please do let me know how do we need to zone this system in the VRP calculator and document. Thanks Nandana

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 03/05/2014 - 00:19

Yes you need to zone the space in the VRP. Is the AHU's air ducted to the room directly or into the Cassette unit. If the former then just proceed as if the cassette is not there. It is just conditioning the air not changing the ventilation rates.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.