In the proposed building there is a semiheated space (climate zone 4, heating power 40 W/m^2, no ventilation, no cooling). In the baseline model shall that space be modeled without HVAC system?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5922 thumbs up
October 25, 2012 - 10:07 am
Yes, only conditioned space needs to be modeled with an HVAC system. See Table G3.1-1 (Baseline) (b).
So in semi-heated spaces the baseline gets modeled identically to the proposed with the same heating type, capacity ratios, fan volume, and fan power.