ROOF CORRIDORS WITH MULCHING

I'm pursuing the credit with the 50% of vegetated roof but the landscape architect considered almos 1500 sq ft. of gravel and rocks for corridors, without this 1500 sq. ft. I can't achieve the 7400 sq. ft total area of vegetated roof. I want to keep the corridors for users, but I need to know if mulching can be taken into consideration to fullfill this remaining sq. footage needed to accomplish the credit. Rocks and gravel are natural and I can't prove the SRI of this materials, what do you suggest?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 03/21/2013 - 14:43

The reason that vegetated roofs are valued so highly in this credit is that the plants' ability to absorb heat and undergo evapotranspiration improves the urban heat island effect. Rock and gravel, while "natural", are not living and do not perform the same function. The roof overall would need to comply with the weighted vegetated / SRI calculation -- but if you get most of the way there with a green roof, you may need very little cool roof. Keep in mind that you can eliminate area for appurtenances and mechanical equipment from the calculation.