Hello,
If in the proposed building there are plenums specified as return air path in the HVAC system, should I use them or ignore them in the baseline model?
Thank you,
Forum discussion
NC-2009 EAc1: Optimize Energy Performance
Hello,
If in the proposed building there are plenums specified as return air path in the HVAC system, should I use them or ignore them in the baseline model?
Thank you,
LEEDuser is supported by our premium members, not by advertisers.
Go premium forTo post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
August 20, 2013 - 10:40 am
You can ignore them as Appendix G does not specify the nature of the returns. Whether the returns are ducted or plenum only makes a difference in the baseline fan power calculations when applying that pressure drop adjustment (which you can't take if you don't have ducted returns in the design).