Forum discussion

NC-v4 EQc1:Enhanced indoor air quality strategies

Restaurant and Kitchen

I need to know if I have to apply interior cross-contamination prevention on a kitchen and a restaurant at my NC office building or not?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 09/01/2023 - 10:47

Hello Omar,  Did you have already the answer to this question? i'm in the same situation as you. We have locker room in hotel, kitchennette, toilets and i dont know if we must make exaust air for this spaces.

Mon, 04/22/2024 - 01:04

Hi all,

Yes, interior cross-contamination prevention shall be applied in kitchen, restaurant, locker room, kitchenette, toilets (if the mechanical and mix-mode ventilation system is used). As stated on LEED v4 guide page 646, it is required to sufficiently exhaust each space where hazardous gases or chemicals may be present or used, to create negative pressure with respect to adjacent spaces when the doors to the room are closed.

The minimum exhaust rate required for these spaces are follows:
- kitchen-commercial = 0.70 cfm/ft2
- kitchenette = 0.30 cfm/ft2
- locker room = 0.50 cfm/ft2
- private toilet = 25/50 cfm/unit
- public toilet = 50/70 cfm/unit

Exhaust rates for these spaces must be maintained at all times, even when the building is not occupied. Please refer to ASHRAE 62.1–2010, Table 6-4, for lists exhaust rate of numerous spaces.

Best regards – Afogreen Build Team

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.