Do we need to include section views with lines of sight drawn from 42" aff to perimeter glazing for every single regularly occupied space within the building, or are the section views only for spaces that may have obstructions (cubicles, tables, reception desks, etc.)?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 04/25/2013 - 13:47

I usually provide sections that represent the typical condition and then any spaces in which i think could be questioned. Such as interior space looking through another space, spaces with fixed partitions and shelvings. or non-typical window conditions. Typically, one or two building sections that are either dimensioned or have the 42" labeled should be sufficient. If a reviewer has a question about a specific sight line, they usually ask.