FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

questions about additional HVAC system in kitchen

Our project is a high rise building, which consists of offices, bank, dining area and so on. Now it is under the LEED V3 CS review. I have a question about the spaces which are not normally conditioned. In our proposed building, kitchens are designed as unconditioned spaces, which only contain exhaust fans and supply fans. So I set these spaces as unconditioned zone in both proposed and baseline model, and put the fan power in the electric meter directly to calculate the energy cost of these fans. The technical advice of reviewer told that an additional HVAC system type should be reflected in the baseline model for the kitchens. I know that according to the exception (b) of Section G3.1.1, additional system types must be included in the Baseline model if some spaces have occupancy or process loads or schedules that differ significantly from the rest of the building.(e.g., data/telecom rooms, kitchens, movie theaters), but in this project, the kitchens are unconditioned spaces, no cooling and heating system is used in the kitchen. The question is that if I use system3 or system4 in the baseline model, can I keep the kitchens in the proposed model still as unconditioned spaces? Or should I add the same system in the proposed model? I feel so confused about this question, looking forward to the help and advice

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 08/30/2016 - 13:53

The Proposed gets modeled as designed according to G3.1-1 Proposed (a) so do not add a system to the kitchen. Even though the kitchen does not have a separate conditioning unit perhaps it is considered indirectly conditioned (conditioned air coming from adjoining spaces) by the reviewer. Personally I think you might have a case for arguing that the baseline should not have a system since the proposed does not as this is the conservative approach. If you want to take this route I would suggest you contact the reviewer and make your case to be sure it will be OK before resubmitting. Alternatively add the system in the baseline to the kitchen. It will only increase your baseline energy use and therefore increase your savings.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.