Purchased Condenser Water

Hello,

I am working on a project that has 2 buildings each one will be submitted to LEED as a separate project. The first building is an office building that is served by water cooled self-contained units. The second building is a residential building that is served by water source heat pump. The first two floors of the residential building are retail spaces served by WSHPs. The WSHP of the retail spaces are connected to the office building condensing plant via a heat exchanger and there will be an energy meter to measure the energy cost. ASHRAE 90.1 does not have guideness about purchased condensing water. I am thinking of modeling the same condensing plant equipment of the office building for the retail spaces to account for the energy cost, is this a reasonable approach? The other option I am thinking of is modeling the retail spaces with the same system as the baseline.

Thank you, 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 01/14/2022 - 16:07

I would recommend modeling each building with a "virtual" condensing plant sized for the condensing loads of that building only. This would be similar to Option 1, Path 2: Full DES Performance Accounting in the reference guide. Alternatively, you could model both buildings in one model and sub-meter each building's energy use separately. 