FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

A portion of our building envelope is historic. Can we exclude it from our model?

Our project has a diesel backup generator. Should we include it in our energy model?

For an existing building, do I need to rotate the model?

Can SHGC be higher in the proposed than in the baseline model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Do I need to justify the electrical and fuel rates I am using in my model?

Our process load is higher than 25%. Do we have to justify that?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

proposed model fan power

We have received our Design Final Review comments and the LEED reviewer has denied EAp2 because the proposed equipment capacities do not match the equipment schedules on the HVAC drawings. Our review comment indicates that the proposed fan power values should match the nominal horsepower for these motors per the mechanical schedules. I feel that this is incorrect. The proposed model should be based on the brake horsepower values, not the nominal motor horsepower values. Please let me know if I am incorrect about this. Also, is there a CIR or other documentation that I can mention in our appeal.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 06/11/2015 - 16:43

It should be BHP. The Proposed model should match the mechanical schedule and if it does not then an explanation should be provided. If the schedule includes just HP and the models indicates something else, like kW, the reviewer should make an assumed adjustment to HP to estimate BHP before converting to kW. We usually use about 85% then 0.746kW/HP. So if you do not provide the BHP. No interpretation or other documentation should be needed for a HP-BHP-kW calculation. You could send a project team inquiry to GBCI about the review comment if you think the reviewer was in error.

Wed, 05/03/2017 - 19:17

Hi Markus, For clarification purposes. You are saying that for the conversion of fan/pump bhp to KW we should use: Fan KW = (bhp x 0.7457 KW) / motor efficiency (ex. 85% or 65% etc). Please confirm. Thanks, Maria

Wed, 05/03/2017 - 19:42

That gets you close.