Forum discussion

NC-2009 EAc1:Optimize energy performance

Proposed Building Boiler Plant / Baseline Building System

Hello, In the proposed building simulation, some of the spaces are not yet defined and therefore are being simulated as office spaces with System 3 - PSZ-AC. Because there is a boiler plant in the building for HVAC & SHW it should be assumed that the heating source for this System 3 - PSZ-AC is obtained from this plant (with higher efficiency than the baseline building reference boiler plant). Correct? Best regards.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 01/10/2013 - 19:09

You cannot just assume a system 3 for undefined proposed spaces unless that matches the baseline system. In the absence of a system design the proposed spaces must be modeled identical to the baseline.

Fri, 01/11/2013 - 10:37

Hello Marcus, In the case of a System 5 (Packaged VAV with reheat) for both baseline and proposed buildings for undefined spaces. In the proposed building energy simulation should we: 1) Consider that all heating energy is provided by the actual boiler plant (with the high efficiency boilers of the project). In this case, the VAV units would have heating coils connected to this plant. 2) Or should we consider a separate boiler plant with efficiencies such as in Table 6.8.1F. In the second case, no energy savings are obtained in the heating consumption of these spaces even if the actual boiler plant is designed with spare capaciy (accounting for spaces which are not yet defined). Best regards.

Fri, 01/11/2013 - 15:51

If the HVAC in these spaces has not yet been designed it must be identical to the baseline. So #2.

Fri, 01/11/2013 - 17:09

Thanks.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.