CI-2009 IEQp1:Minimum IAQ Performance

Project can't meet Outside Air Requirements

We have a project which the outdoor air supply is limited from the base building HVAC system (out of our boundary) and we are not sure if the project will be able to meet the ASHRAE 62.1 requirements due to this. Has anyone gone down the compliance path when one or more AHUs are unable to meet the ASHRAE 62.1 requirement and had their credit approved? I'm wondering what GBCI considers qualifying 'space and system constraints' and requires for documentation.

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 08/31/2012 - 17:44

If there are space and system constraints, you can go down to 10 cfm per person, but no less. There's no way around this, without violating the original intent of this pre-requisite.