NC-v4 EAp2:Minimum energy performance

Process energy compliance

Helo al!

We are evaluating the LEED certification potential of a new winery that will be built in Portugal (using the rating system LEED BD+C v4: New Construction and Major Renovation).

The wine production process requires fermentation tanks to be kept at a controlled temperature (below 28ºC).  For that purpose,  these fermentation tanks  (stainless steel, volumes between 6 m3 and 30 m3) have a cooling jacket fed by chilled water (10ºC). Tanks and associated chilled water piping are traditionally not thermally insulated since:

  1. fermentation (and thus tank temperature control) takes place for only a short period of time (about 1 month per year). This circumstance obviously penalizes the payback of thermal insulation.
  2. the building zone where fermentation tanks are located is occupied and does not have any active HVAC system. One of the main reasons why this zone dos not have active an active HVAc system is precisely because fermentation tanks have an indirect space cooling effect (note that even with the contribute of the tanks, indoor air temperatures can reach 30 ºC).
  3.  

The question is: in what concerns ASHRAE 90.1 - 2010 mandatory requirements for thermal insulation (section 6.4.4.1.3):

  • do fermentation tanks need to be thermally insulated? If yes, to which extent?
  • does the chilled water piping in the vicinity of the tanks need to be insulated?

 

Thanks for your attention. I’m looking forward to your reply.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 02/25/2019 - 17:41

This is a process load so it is not subjected to the thermal insulation requirements of 90.1.

Tue, 02/26/2019 - 10:57

Thank you for quick reply Marcus!   Can you please clarify where it is stated that process loads are exempted from 90.1 compliance?   Please note that: 1) ASHRAE 90.1 - 2010 scope states that it applies to "new equipment or building systems specifically identified in this standard that are part of industrial or manufacturing processes"; 2) Even though fermentation tanks cooling is a process load, chilled water for tank jacket cooling is produced in a chiller that is also use for air conditioning of administrative areas.    Thanks in advance,    

Thu, 02/28/2019 - 17:37

Thanks for challenging my reply. I looked and I think I was wrong. The scope of the standard expanded from 2007 to 2010 to now include equipment and systems cover by the standard related to process loads. So if the standard says this needs to be insulated, then yes it needs to be insulated! Of course if you can find an exception that applies it could be exempt.

Fri, 03/01/2019 - 10:50

Thanks again Marcus!   I can´t figure out any exemption that could apply (since unfortunetely there isn´t any exempetion associated with payback criteria). The only remaining doubt is if 6.4.4.1.3 may only apply to piping (therefore fermentation tank could be excluded). What is your opinion? If thermal insultation is required in the fermentation tank, what would be the required thickness (table 6.8.3.B is only for pipes) Kind regards,

Mon, 03/04/2019 - 22:02

Yea I do not see anything that covers the tank.