Forum discussion

EBOM-2009 IEQp1:Minimum indoor air quality performance

Problems with version 3 of the Form and Vot

RE: IEQp1 Form Table. Case 1: ASHRAE 62.1-2007 Ventilation Rate Procedure (LEED O&M v3) I fill out the table based on the critical zone for that AHU, but the Form(Version 3) automatically calclulates and enters Vot ( even though it doesnt have sufficient information )-- rather that letting me input Vot from the LEED calculator spreadsheet. Either I totally misunderstand the table, or it is goofy - anyone else having this issue ??

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 08/24/2011 - 11:13

Table "Case 1: ASHRAE 62.1-2007 Ventilation Rate Procedure" auto-calculates Rp, Ra, Vbz, Voz, and Vot. If you are are using a different calculation / spreadsheet to show compliance check the "The project team is using an alternative compliance approach in lieu of standard submittal paths" box under the ADDITIONAL DETAILS heading on the template.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.